Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Learn about the Community. Join our Core Community to Get Started
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Unable to read any public signals from TAC Xenta 300/400/280 in a TAC Xenta 511, but SNVTs from TAC Xenta 100 controllers are fine.

Issue

Unable to read any public signals from TAC Xenta 300/400/280 in a TAC Xenta 511, but SNVTs from TAC Xenta 100 controllers are fine.

Environment

  • Xenta Programmables
  • Xenta 511
  • Xenta 100 series ASCs

Cause

The TAC Xenta 511 is not a member of the TAC Vista group.

Resolution

  1. Go to the System plug-in
  2. Choose LNS Network >Create group bindings.
Tags (11)
Labels (1)
No ratings