Unable to override points in a MicroZone II from an I/A Series (Niagara) G3 station. Get error window showing " javax.baja.sys.ActionInvokeException..."

Issue

Unable to override points in a MicroZone II from an I/A Series (Niagara) G3 station.

Get error " javax.baja.sys.ActionInvokeException   at com.tridium.fox.sys.broker.BFoxComponentSpace$FoxTrapCallbacks.invoke(BFoxComponentSpace.java:355)... 

... at java.awt.Component.dispatchEventImpl(Unknown Source)  com.tridium.fox.session.ServerException: java.lang.RuntimeException: Invalid response during override.  Check username and password"

Environment

I/A Series (Niagara) G3 station with the tacAsd driver

I/A Series Network 8000 ASD controller (MicroZone II, PEM-1, LIM)

Cause

The "User Name" and "User Password"  in the Property Sheet of the ASD device object (under the AsdNetwork object) in the ENC's station, and the USRn and PASn stored in the MicroZone II, PEM or LIM database do not match exactly.

The USRn and PASn are case sensitive, accepting ONLY capitalized characters.

The AsdZone2 device property sheet in the G3 station allows entry of lower case characters, which can cause a mismatch in the User Name or User Password, or both.

Resolution

Be sure to enter the correct User Name and User Password in the Property Sheet of the AsdZone2 device, and remember to use ONLY capital letters.