New in the Community? Get started here

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 
Announcements

- Who are the top users of September? Discover them here!

- Check out the ESS Active Energy Management Blog now! 

- Join us on October 23rd for a live Panel session to discuss The Power of a Sustainable Ecosystem with Hervé Coureil, Chief Digital Officer of Schneider Electric and other great speakers. Register here!

Unable to access to JACE-645 via its Ethernet Port

Issue

Unable to access to JACE-645 via its Ethernet Port. The following is seen when connected to the JACE's Serial Shell.

SerialOut1.PNG

SerialOut2.PNG

SerialOut3.PNG

Product Line

TAC I/A Series

Environment

JACE-645 (TRD-T-645)

Cause

The boot sector of the nand flash has become corrupt and/or the nand flash chip may have failed.

Resolution

The unit cannot be recovered in the field. The options are:

  1. An attempt can be made to re-image the unit but this may not be always successful. Contact Product Support for further details.
  2. Replace the unit. Refer to PA-00502 - End of Commercialization for JACE 600 and JACE 700 for replacement options.
Tags (1)
Labels (1)
No ratings