Issue

Trying to talk to Trane Controller (MP580) and will not update. (LON)

Environment

G3/R2 Niagara

Cause

Run Frequency is a property that defines how often the program executes. If set to 0 values will not update in LON shadow object.

Resolution

Run frequency to a value other than 0.