Transitioning Belimo Bacnet b3865 VAV controllers to an Automation Server

Issue

Transitioning from Continuum to Struxureware Building Operation and replacing bCX's with Automation Servers.
 

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

  • b3865
  • Struxureware Building Operation

Cause

Unsure if the older belimo style VAV controllers are compatible with StruxureWare Building Operation.

Resolution

All of the b3xxx controllers (including both the -V and non -V) will work with the Automation Server under it's MSTP network.

Also check out the b3 VAV Quick Start Video on the Community.