Time Change errors in b3 Trend log data.

Issue

The following time change errors are appearing in the trend data from b3 controller.    

Environment

Trend logs

Cause

b3 firmware was at 4.500029.  Current release is 4.500076

Resolution

The issue was corrected by upgrading all b3 controllers to 4.500076.