Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Learn about the Community. Join our Core Community to Get Started
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

The time of DCU will change automatically for specific period

Issue

Under multiple PC environments, the time of a DCU changes automatically for a specific period. The time of the Server/Filemaster is correct.

Product Line

TAC INET

Environment

  • I/NET
  • Multiple PCs environment

Cause

For multiple PC environments, the time setting of each PC does not synchronize. The time of Server/Filemaster is correct, but the time of Remote Client/Equalized Client may be not correct. If there is a DCU Synchronization function set on the Remote Client/Equalized Client, the wrong time will synchronize to the DCU for specific period set in the function of DCU Synchronization.

Resolution

Synchronize the time on Remote Client/Equalized Client with Server/Filemaster through NTP or manually. The other way is only to set DCU Synchronization function on Server/Filemaster, not on Remote Client/Equalized Client.

The NTP as of March 1, 2013 no longer works. See Time sync is no longer working for suggestions

Tags (7)
Labels (1)
No ratings