Learn about the Community. Join our Core Community to Get Started

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Test Connection fails when creating VideoServer object in Continuum 1.9x

Issue

Cannot connect to video server when creating a VideoServer object in Continuum and Test Connection is selected.

Product Line

Andover Continuum, Pelco

Environment

  • Continuum
  • DSConnex
  • Digital Sentry

Cause

Patch not installed for DSConneX versions 4.3 and 7.x not working with Andover Continuum 1.91 or 1.92 or LAN connection problems

Resolution

Install v1.91 DSConneX Video Patch hotfix for issue with DSConneX versions 4.3 and 7.x not working with Andover Continuum 1.91.

For 1.92 these files are included, so if the error is still occurring, then there are LAN connection issues.

Tags (1)
Labels (2)
No ratings