Temperature sensor input is not changing.

Issue

Temperature sensor input point is not updating. Sensor works fine on another input.

Environment

i2 controller

Cause

The threshold may be incorrectly set. For example, if it is set to 10 instead of 0.1.

Resolution

Check the threshold and make sure it is set to 0.1.