Issue
TS-5722 and TS-6722 30 K thermistor sensors with 11 K shunt resistance table
Environment
- TS-5722 Electronic Remote Temperature Sensors
- TS-6722 Electronic Remote Temperature Sensors
Cause
Specification on the sensing element.
Resolution
Temp (°C) | Temp (°F) | Ohms (11K shunt) |
25.0° | 77.0° | 8,049 |
26.0° | 78.8° | 7,960 |
27.0° | 80.6° | 7,872 |
28.0° | 82.4° | 7,782 |
29.0° | 84.2° | 7,691 |
30.0° | 86.0° | 7,599 |
31.0° | 87.8° | 7,507 |
32.0° | 89.6° | 7,413 |
33.0° | 91.4° | 7,319 |
34.0° | 93.2° | 7,224 |
35.0° | 95.0° | 7,129 |
36.0° | 96.8° | 7,033 |
37.0° | 98.6° | 6,936 |
38.0° | 100.4° | 6,839 |
39.0° | 102.2° | 6,742 |
40.0° | 104.0° | 6,644 |
41.0° | 105.8° | 6,546 |
42.0° | 107.6° | 6,448 |
43.0° | 109.4° | 6,350 |
44.0° | 111.2° | 6,251 |
45.0° | 113.0° | 6,153 |
46.0° | 114.8° | 6,055 |
47.0° | 116.6° | 5,957 |
48.0° | 118.4° | 5,859 |
49.0° | 120.2° | 5,762 |
50.0° | 122.0° | 5,665 |
51.0° | 123.8° | 5,568 |
52.0° | 125.6° | 5,472 |
53.0° | 127.4° | 5,376 |
54.0° | 129.2° | 5,280 |
55.0° | 131.0° | 5,186 |
56.0° | 132.8° | 5,092 |
57.0° | 134.6° | 4,999 |
58.0° | 136.4° | 4,906 |
59.0° | 138.2° | 4,815 |
60.0° | 140.0° | 4,724 |
61.0° | 141.8° | 4,634 |
62.0° | 143.6° | 4,545 |
63.0° | 145.4° | 4,457 |
64.0° | 147.2° | 4,370 |
65.0° | 149.0° | 4,284 |
66.0° | 150.8° | 4,199 |
67.0° | 152.6° | 4,114 |
68.0° | 154.4° | 4,032 |
69.0° | 156.2° | 3,951 |
70.0° | 158.0° | 3,870 |
71.0° | 159.8° | 3,791 |
72.0° | 161.6° | 3,713 |
73.0° | 163.4° | 3,635 |
74.0° | 165.2° | 3,559 |
75.0° | 167.0° | 3,484 |
76.0° | 168.8° | 3,411 |
77.0° | 170.6° | 3,339 |
78.0° | 172.4° | 3,268 |
79.0° | 174.2° | 3,198 |
80.0° | 176.0° | 3,130 |
81.0° | 177.8° | 3,061 |
82.0° | 179.6° | 2,995 |
83.0° | 181.4° | 2,931 |
84.0° | 183.2° | 2,868 |
85.0° | 185.0° | 2,805 |
86.0° | 186.8° | 2,743 |
87.0° | 188.6° | 2,683 |
88.0° | 190.4° | 2,625 |
89.0° | 192.2° | 2,567 |
90.0° | 194.0° | 2,510 |
91.0° | 195.8° | 2,454 |
92.0° | 197.6° | 2,400 |
93.0° | 199.4° | 2,346 |
94.0° | 201.2° | 2,294 |
95.0° | 203.0° | 2,243 |
96.0° | 204.8° | 2,193 |
97.0° | 206.6° | 2,143 |
98.0° | 208.4° | 2,096 |
99.0° | 210.2° | 2,048 |
100.0° | 212.0° | 2,002 |
101.0° | 213.8° | 1,958 |
102.0° | 215.6° | 1,915 |
103.0° | 217.4° | 1,872 |
104.0° | 219.2° | 1,831 |
105.0° | 221.0° | 1,790 |
106.0° | 222.8° | 1,750 |
107.0° | 224.6° | 1,711 |
108.0° | 226.4° | 1,673 |
109.0° | 228.2° | 1,635 |
110.0° | 230.0° | 1,599 |
111.0° | 231.8° | 1,563 |
112.0° | 233.6° | 1,528 |
113.0° | 235.4° | 1,494 |
114.0° | 237.2° | 1,461 |
115.0° | 239.0° | 1,429 |
116.0° | 240.8° | 1,397 |
117.0° | 242.6° | 1,366 |
118.0° | 244.4° | 1,336 |
119.0° | 246.2° | 1,306 |
120.0° | 248.0° | 1,278 |
121.0° | 249.8° | 1,249 |