Learn about the Community. Join our Core Community to Get Started

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

System alarm message, Physical device not defined/configured

Issue

System alarm message, Physical device not defined/configured, in the alarm window.

Product Line

TAC Vista

Environment

TAC Vista (all versions)

TAC Xenta programmable controllers

Cause

This message is displayed when there is a TAC Xenta 401/30x/28x that is attached to the physical network, but the name is not in the TAC Vista database. It is there to alert that there are unconfigured controllers on the network.

Resolution

  • Download to the controller from TAC Vista
  • Remove the controller if it is not needed.

For an alternative cause and resolution for the message, see Physical device not defined/configured.

Tags (9)
Labels (1)
No ratings