StruxureWare Building Operation Runtime Compatibility available during Upgrades

Issue

  • Is it supported to access an Automation Server 1.4.0 with the Workstation 1.4.1?
  • Are there any problems and what features are supported when accessing a 1.4.0 Automation Server with WorkStation 1.4.1?

Environment

Enterprise Server / Workstation 1.4.1

Automation Servers 1.4.0, 1.3 with SP1 and SP2

Cause

Understanding of the new Runtime Compatibility mode available in 1.4.1 available during system upgrades

Resolution

Building Operation supports runtime compatibility between servers running two versions on a single system, during an upgrade process. Version 1.4.1 servers are runtime compatible with version 1.3 SP1 and 1.3 SP2 servers. The system is able to exchange runtime information between 1.4.1 servers and 1.3 SP1 or 1.3 SP2 servers. However, configuration changes cannot be made from an upgraded WorkStation via an upgraded Enterprise Server to a non upgraded Automation Server, such as creating, configuring, and deleting objects. There is also no runtime compatibility for WebStation.

Runtime compatibility means you can delay the upgrade of some Automation Servers running version 1.3 SP1 or 1.3 SP2 while upgrading the Enterprise Server, WorkStation, Reports Server, and some Automation Servers to version 1.4.1.

You cannot make any configuration changes on an Automation Server running the 1.3 SP1 or 1.3 SP2 version with WorkStation and Enterprise Server running the 1.4.1 version. However, you can make the changes using a parallel WorkStation running a 1.3 SP1 or 1.3 SP2 version that is connected to the Automation Server running the 1.3 SP1 or 1.3 SP2 version.

Full compatibility is supported on Automation Servers running the 1.4.0 version  

Additional detail is available on the Online Help http://help.sbo.schneider-electric.com/topics/show.castle?id=9807&locale=en-US&productversion=1.4&a=...

Supported Features:

Navigate
You can navigate in the system tree of an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. However, object and property types removed in the 1.4.1 version compared to the 1.3 SP1 or 1.3 SP2 version are not be displayed in the system tree.

Search
You can perform an object or property search on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. However, object and property types removed in the 1.4.1 version compared to the 1.3 SP1 or 1.3 SP2 version are not be displayed in the search list.

View Events
You can view detailed information and perform commands on events on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. The 1.4.1 Enterprise Server will also store events from an Automation Server running 1.3 SP1 or 1.3 SP2 version.

View Trend Logs and Trend Charts
You can view trend log lists and trend charts on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. Extended trend log lists in the server running 1.4.1 version are functional and be able to retrieve values from a server running the 1.3 SP1 or 1.3 SP2 version.

View Graphics
You can navigate to and view a graphic on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server at 1.4.1 version. Graphic variable values can be changed with Graphics Editor, but configuration data cannot be changed.

View Alarms
You can view detailed alarm information from an Automation Server running the 1.3 SP1 and 1.3 SP2 version, with WorkStation and Enterprise Server at 1.4.1 version. Also actions on alarms can be performed, such as assigning or disabling an alarm and enabling a Change-state logging.

View Dynamic Values
You can navigate to and view dynamic values in the Watch pane from an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. However, because there is no way to navigate to and view objects or properties that have been removed in the 1.4.1 version, such dynamic values cannot be viewed.

Transfer Values
You can transfer values from an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with an Enterprise Server or Automation Server running the 1.4.1 version and the other way around.

Change and Force Variables
You can change and force variables using properties on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version.

Lead and Shadow relationships
Lead and Shadow relationships work for all objects with the runtime compatibility support.

Backup
You can make a backup of an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. Log on to the Enterprise Server and then make a backup of the Automation Server running the 1.3 SP1 or 1.3 SP2 version. You can also log on directly to the Automation Server running the 1.3 SP1 or 1.3 SP2 version with WorkStation running the same 1.3 SP1 or 1.3 SP2 version, and then make a backup of the Automation Server.