SmartStruxure integration to StruxureWare Data Center Expert via EcoStruxure WebServices

Issue

SmartStruxure integration to StruxureWare Data Center Expert via EcoStruxure WebServices

Environment

StruxureWare Building Operation EcoStruxure Web Services

StruxureWare Data Center Expert 7.2.0

Cause

There is a need to have StruxureWare Building Operation pass data to StruxureWare Data Center Expert using EcoStruxure Web Services. StruxureWare Building Operation Web Services is capable of both 'Serve' and 'Consume' functionality. However, StruxureWare Data Center Expert (version 7.2.0) is only capable of Web Services 'Serve' function.

Resolution

Use Modbus TCP instead of EcoStruxure Web Services if StruxureWare Data Center Expert is required to read from StruxureWare Building Operation. 