SmartStruxure Lite shows offline in StruxureWare Building Operation

Issue

When the EWS interface is created, the Status show "online". However, after clicking on the Hardware > EcoStruxure Web Service > SSLite, the Status will go offline.

Product Line

EcoStruxure Building Expert, EcoStruxure Building Operation

Environment

  • StruxureWare Building Operation 1.3 and above
  • SmartStruxure Lite 2.7 and above
  • EcoStruxure Web Services

Cause

Make sure the SOAP Endpoint field says "ews" and not "EWS". Lua program is a case sensitive program.

Resolution

Change the SOAP Endpoint field to "ews".