Setpoints and Commands from Niagara objects are not being written to the BACnet points

Issue

Setpoints and Commands from Niagara objects are not being written to the BACnet points

Environment

I/A Series R2 WorkPlace Pro and UNC
I/A Series MNB controllers

Cause

The BACnet objects are located in a PollOnDemand container. BACnet objects in the PollOnDemand container will only be polled when linked Gx objects (graphics) are viewed. In this particular case, these BACnet objects are not required to be displayed on graphic pages and thus they are not linked to any Gx objects. 

being viewed

Resolution

Create GxText objects in the PollOnDemand container and link the BACnet objects' outputs to the GxText objects. With this, the BACnet objects will be polled when the PollOnDemand container is viewed. 