Server/Client

Issue

Running Server/Client on a system

Environment

I/Net Seven version 2.13 and above.

Cause

Server client on a system that is running on different versions and not working.

Resolution

For Server/Client to work on a system, I/Net has to be installed on all the PCs and they all must be the same version as well. The following steps needs to be followed to configure this correctly:

  1. The Host PC that will be acting as the Server must have the current database.
  2. Modify the active profile in the Configuration Editor
  3. In the WorkStation Options, set this to be Standalone
  4. On the other PCs, this would be set to Remote Client
  5. An editor will come up stating the "the database will be replaced"
  6. Click on the proceed button to connect to the Server.
  7. Once completed, the client PCs would now be looking at the Server