Script error when navigating menu in TGML graphic in 1.4, graphic was working fine in 1.3.

Issue

In  releases prior to 1.4 graphic objects weren't unloaded when navigated away from. This has been fixed in 1.4.

As a result of this change, If a TGML has a navigate in a script(by using invoke) this could cause a script error if there are scripts on parent elements.

Environment

Workstation

Enterprise Server

Automation Server

Cause

Documentation

Resolution

Open the graphic in source mode and add evt.stopPropagation(); before the invoke in the Click() function.

 

IMPORTANT:

For a an updated version of the component without the error click the link below to go to the community.

 http://buildingscommunity.schneider-electric.com/docs/DOC-7279