SPU1201 and SPU1202 obsolescence

Issue

SPU 1201 Universal Pressure Switch – Specification No. 131-1-201
SPU 1202 Universal Pressure Switch – Specification No. 131-1-202

Environment

Site requesting a Universal Pressure Switch

Cause

SPU1201 and SPU1202 obsolescence

Original pdf specification sheet is available HERE.

Resolution

We have made the SPU1201 and SPU1202 obsolete per the supplier.  The closest replacement options that we have are listed below:
 
• SPU1201 is a 0.2 – 4.0 Bar device.  The replacement options are:
o SPP930-2200: This is a  0.12 – 2.2 Bar device.
o SPP930-6000: This is a 1.0 – 6.0 Bar device.
• SPU1202 is a 12 – 250 mBar device.  The replacement options are:
o SPP930-2200: This is a  1200 – 2200 mBar device.
o SPP930-6000: This is a 1000 – 6000 mBar device.
We have made the SPU1201 and SPU1202 obsolete per the supplier.  The closest replacement options that we have are listed below:
 
• SPU1201 is a 0.2 – 4.0 Bar device.  The replacement options are:
o SPP930-2200: This is a  0.12 – 2.2 Bar device.
o SPP930-6000: This is a 1.0 – 6.0 Bar device.
• SPU1202 is a 12 – 250 mBar device.  The replacement options are:
o SPP930-2200: This is a  1200 – 2200 mBar device.
o SPP930-6000: This is a 1000 – 6000 mBar device.
We have made the SPU1201 and SPU1202 obsolete per the supplier. The closest replacement options that we have are listed below:
• SPU1201 is a 0.2 – 4.0 Bar device. The replacement options are:
- SPP920 Series
• SPU1202 is a 12 – 250 mBar device. The replacement options are:
- SPP920 Series
 
Please refer to the Product Announcement for the SPP920 series Differential Pressure Switches for neutral and slightly aggressive liquids and gases.