Issue

  • SPU 1201 Universal Pressure Switch – Specification No. 131-1-201
  • SPU 1202 Universal Pressure Switch – Specification No. 131-1-202

Product Line

Field Devices

Environment

Site requesting a Universal Pressure Switch

Cause

SPU1201 and SPU1202 obsolescence

Original PDF specification sheet is available here: DS21602-0203.pdf.

Resolution

The SPU1201 and SPU1202 have been made obsolete per the supplier. The closest replacement options that we have are listed below:

  • SPU1201 is a 0.2 – 4.0 Bar device. The replacement options are SPP920 Series
  • SPU1202 is a 12 – 250 mBar device. The replacement options are SPP920 Series

Refer to Product Announcement PA-00166 for the SPP920 series Differential Pressure Switches for neutral and slightly aggressive liquids and gases.