SECURITY EXPERT: Turned off the backup function to not back up a server but still backing up the event database.

Issue

Turned off the "Backup Main Database Every Night" to stop back up of a server but it is still backing up the event database.

Product Line

Security Expert

Environment

Security Expert Server

Cause

Even though the "Backup Main Database Every Night" option is turned off, the "Event Database"->"Generate Differential Events Backup" is running ever night. 

Resolution

Log on to the Security Expert System then go to Global->General-> under the events tab. Uncheck/remove the "Generate Differential Events Backup" option along with "Backup Main Database Every Night".  The event's backup will stop.