New in the Community? Get started here

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 
Announcements
Discover the Exchange Community Top members of July 
Discover the latest features your community has to offer: register to the webinar here

SE7000 Series RS-485 transceiver unit load

Issue

SE7000 Series RS-485 transceiver unit load

Product Line

EcoStruxure Building Expert, EcoStruxure Building Operation

Environment

SE7000 series room controllers

Cause

The room controller RS-485 transceiver unit load is not included in the data sheets. This information is needed to determine the number of BACnet MS/TP devices per RS-485 segment.

Resolution

Refer to Application Note AN05-RS485-VT7000 and Quick Guide RS485-VT7000. The links to these documents can be found in MS/TP and Modbus RS485 Communications on StruxureWare Automation Server

Tags (4)
No ratings