New in the Community? Get started here

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 
Announcements
Discover the Exchange Community Top members of July 
Discover the latest features your community has to offer: register to the webinar here

Return to Normal Email Notification is only delivered when the Return to Normal notification is acknowledged at the Workstation.

Issue

While email notifications for alarm conditions are being delivered promptly, Return to Normal notifications are not delivered until the notification is acknowledged at that the workstation.

Environment

  • AS
  • ES
  • Email Notification

Cause

Email Notification is not configured correctly.

Resolution

Select the Reset checkbox to have an email delivered when the alarm condition clears.

The Normal box should read "Acknowledged Normal" since this delivers a notification that the Off Alarm notification has been acknowledged.

Tags (4)
Labels (1)
No ratings