Replacement of VTR Valve Body by VTRE or MB/MBF Valve Body due to obsolescence.

Issue

VTR Valve Body requires replacement due to obsolescence.

Environment

  • VTR
  • 3-port
  • Mixing Valve Body

Cause

Obsolescence of VTR Valve Body.

Resolution

VTR Valve Bodies are obsolete and have been for many years. 

VTR Valve Bodies were available with either Flanged or Screwed connections.  Details of the various size / connection combinations available appear here

 

REPLACEMENT OF VTR FLANGED CONNECTION VALVE BODY 

A replacement for the VTR Flanged Valve Body (20-150mm only) may be selected from the VTRE range of Flanged Valve Bodies, details of which appear here.  

N.B.

It should be noted that the VTRE Valve Body is rated PN6 whereas the VTR was rated PN10.

The VTRE Flanged Valve Body may be operated by the EM9 Actuator, details of which appear here.

Alternatively the VTRE Flanged Valve Body may be operated by the M9B Actuator, details of which appear here.

No Linkage Kit is required to mount the EM9 or M9B Actuator on the VTRE Flanged Valve Body.

Alternatively a replacement for the VTR Flanged Valve Body (65-100mm only) may be selected from the MBF range of Flanged Valve Bodies, details of which appear here.

N.B.

It should be noted that the MBF Valve Body is rated PN6 whereas the VTR was rated PN10.

The MBF Flanged Valve Body may be operated by the MD20B series Actuator, details of which appear here.

Alternatively the MBF Flanged Valve Body may be operated by the MD20A Actuator, details of which appear here.

A Linkage Kit (914-1070-000) will also be required, details of which appear here.

 

REPLACEMENT OF VTR SCREWED CONNECTION VALVE BODY 

A replacement for the VTR Screwed Valve Body (15-50mm) may be selected from the MB range of Screwed Valve Bodies, details of which appear here.

The MB Screwed Valve Body may be operated by the MD10B series Actuator, details of which appear here.

Alternatively the MB Screwed Valve Body may be operated by the MD10A Actuator, details of which appear here.

A Linkage Kit (914-1071-000) will also be required, details of which appear here.