Issue
Priority Value Select object.
The output of Instance 31 of Priority Value Select was always 0 in a MicroNet MN 550 controller. All other instances function correctly.
Environment
MicroNet MN 550 controller
Cause
MicroNet 50 controller must be upgraded to firmware version 5.
Resolution
This has been corrected with MicroNet 50 controller Firmware version 5 released August 2008.
Additional information on firmware 5 can be found in TPA-LOND-08-0014.00