Potentiometer input on a Xenta programmable device

Issue

Setting up a potentiometer or resistance input on a Xenta Programmable controller.

Product Line

TAC Vista

Environment

  • TAC Menta
  • Xenta 280,300 and 400

Cause

No input option is available for a potentiometer or resistance in a Xenta device

Resolution

A curve module can be used to create your own input lookup table, as shown below.

Lookup table.png

Attached file Pot_To_0_100_R01.zip provides an example of this 10K potentiometer sample