Object Transfers are not working after upgrading Vista.

Issue

Object Transfers are not working after upgrading Vista. The devices are online and the values are updated when viewed, but the values aren't transferred via the object transfer objects.

Environment

Vista 5.1.X that has been upgraded.

Cause

The vista server is in engineering mode.

Resolution

Go to the $System object under the TAC Vista root object in workstation and check the  Status-Operating check-box is checked.