No warning or confirmation when AS or ES is deleted in PCT

Issue

In version 1.2.2.22 you don't get a confirmation when the ES/AS is deleted. The AS or ES is gone after clicking on the Delete button.

When an ES or AS was deleted from a project in earlier versions of the PCT you had to enter a password for the admin account as confirmation.

2019-03-28_14-16-26.png

 

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Project Configuration Tool (PCT) version 1.2.2.22

Cause

The confirmation when deleting a device in PCT is taken away in version 1.2.2.22

Resolution

When starting the ES/AS be very careful, the start button is just under the delete button.

2019-03-28_14-30-58.png