Maximum distance between SC3000 and SE7300

Issue

What is the maximum distance between SC3000 relay pack  and SE7300 controller

Product Line

EcoStruxure Building Expert

Environment

  • SC3000 relay pack
  • SE7300 controller

Cause

Depending on installation and site configuration, the max distance between units may be of interest.

Resolution

This hasn't been tested, but at least 100 ft (30 m) with 22 GA or bigger wire.

For additional details, also please see Which models of the SE7300 series room controllers can be used with the SC3000 series relay packs?