MSTP Status object causes Device Learn failure at the UNC

Issue

Added the MSTP Status object to the MNB-1000 database and connected a constant tag to its network input and tested it with WorkPlace Tech and it functions as expected.  However, when doing a Device Learn of this MNB-1000 at the UNC it fails. 

The messages is "Learn Device Failed. ObjectId [binary_value:589834]".   The instance number after the binary_value may be different depending on other status objects in the database.

Environment

I/A Series Niagara R2

Cause

Cause is being investigated. 

Resolution

Use the Device Status object instead.  It will perform the same function and can be learned at the UNC without issue.