Limit the setpoint offsets of an STR-350 in "offset" mode

Issue

Can not limit the setpoint offset high and low limits when using "offset" mode in the STR-350.

Environment

STR-350

LonMaker

Cause

When viewing the controller data in degrees Fahrenheit, an offset must be applied to each value.

Resolution

  1. In the plug-in, set the STR to use setpoint offset mode instead of absolute setpoint.
  2. Browse the controller with the LonMaker browser.
  3. Scroll to nciSetpointHigh and nciSetpointLow.
  4. Start from 32 and set your two NCIs as desired.
    For example:  If you wanted your occupant to have the ability to adjust ±5°F, set nciSetpointHigh to 37 and nciSetpointLow to 27.