Issue
In Niagara R2, how can manual commands be issued to Network 8000 GCM/LCM analog and binary points?
The LcmAnalogCmd, LcmBinaryCmd, GcmAnalogCmd, and GcmBinaryCmd objects have a manualCmd field. However, this option does not appear in a web browser.
Environment
Niagara R2
Cause
To use binary and analog commands to control points, connect the objects to an Analog output or Binary object.
Resolution
Due to an anomaly in these objects, connect to an Analog output or Binary Object and issue a change with it before the option to allow issuing a command to the AnalogCmd or BinaryCmd will be available.