New in the Community? Get started here

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 
Announcements

Discover the Exchange Community Top members of August

Infinity Controller shown as online on controller webpage, but offline in Continuum

Issue

When looking at the controller configuration web page of a CX9702, it shows comm status = online, but when in Continuum it shows up as offline.

Product Line

Andover Continuum

Environment

  • CX9702
  • CyberStation

Cause

Controller received a probe from the workstation but Continuum has not been able to acknowledged that the probe was successful.

Resolution

  1. Check that the network ports are all open
  2. Shut down and restart Continuum on the workstation

Or:

  1. Edit controller object in Continuum Explorer
  2. Select Out of Service and Apply
  3. De-select Out of Service and Apply
Tags (1)
Labels (1)
No ratings