In an SCU1284 with a dual address what is the addressing scheme for the "DO's"?

Issue

In an SCU1284 with a dual address what is the addressing scheme for the "DO's"?

Environment

I/NET site with Access Control

Cause

Addressing issue with SCU1284

Resolution

In the Dual Address mode of the SCU1284 the "DO's" addressing scheme is as follows

First four relays are associated with the first address DOxx00 thru DOxx03.

The Last four relays are associated with the second address DOyy00 thru DOyy03