Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now

By Clicking on "Register Now", you acknowledge that you have read the Privacy Notice for Schneider Electric Exchange.

Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

IAC touch screens reset to default address on Sundays

Issue

The address of the IAC touch screen will reset to default (65) on Sundays when time broadcast is used

Product Line

EcoStruxure Building Operation, Satchwell MicroNet

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server
  • MicroNet transition
  • IAC touch screen

Cause

When the time broadcast on an AS or ES MicroNet interface the address of the touch screen will reset

Instead of broadcasting the day number as a 7, the day number is sent as a 0.
The IAC touch screen does not understand day 0, resulting in the touch screen resetting to defaults. No other days are effected.

When the touch screen resets, the touch screen's address is also reset and defaults to address 65.
Unless the touch screen was originally configured as address 65, the controllers on the SubLAN of the touch screen will not be available, until the correct address is entered into the touch screen.

Resolution

A hotfix is available from Product Support for SBO version 1.7.1.12604

This correction has been included in SBO 1.8 and later releases.

Earlier SBO version will need to be upgraded to SBO 1.7.1 with the hotfix applied or upgrade to version 1.8 when available

Tags (5)
No ratings