How to locate and change the LonWorks domain ID

Issue

Where to find the domain ID of a LonWorks Network underneath a LonWorks Interface in a StruxureWare network. The domain can also be changed in this same location.

Environment

  • Workstation

Cause

If the domain ID of a LonWorks network needs to be changed or known for some reason it can be done through the properties of the LonWorks Network.

Resolution

  1. Right click on the LonWorks Network underneath the LonWorks Local Interface.
  2. Click Properties.
  3. Click on the Advanced tab and look at the Domain table for Network Interface. The value in the first row of the ID column is the domain ID in decimal form.
  4. In order to change the domain ID, click on the value and a selectable box will appear. Adjust the domain ID to the desired decimal value.
  5. Click OK.