New in the Community? Get started here

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 
Announcements
Discover the Exchange Community Top members of July 
Discover the latest features your community has to offer: register to the webinar here

How to disable the fan in heating mode with SER7000 | SER8000

Issue

User can’t disable the fan in heating mode

Environment

  SER7000 | SER8000

Cause

 Misconfiguration of the thermostat

Resolution

SER7300

In some application, the device may control baseboard heat or different controls and the user may want to stop the fan in heating mode.

The user shall set the Pulsed HT parameter to ON and Fan Cont to Off Auto and this will solve the issue.

 

SER8300

The user shall set Fan Cont to Off Auto and this will solve the issue.

 

Tags (1)
No ratings