How to bring an MPM-VA online via ZigBee with the MPM Coordinator?

Issue

How to bring an MPM-VA online over ZigBee to communicate with the ZigBee Coordinator (which is also the MPM you have your IP interface with).

Environment

MPM, MPM-VA, ZigBee

Cause

Cannot figure out how to get the MPM-VA to communicate over ZigBee to the Coordinator.

Resolution

Use web interface on the bench to set up ZigBee Pro Extended Configuration on the "remote MPM-VA" to match the Coordinator's Channel, PAN ID, Extended Network ID, Stack Profile, Security Profile and Trust Center Link.

Save settings and save database to flash.

You can now disconnect the IP connection to the remote MPM-VA. Re-discover controllers from the Coordinator MPM. It will appear as a "peer" below the coordinator, i.e., it will not be "under it" like a Room Controller (stat) or TE2.
 