Issue
If an upgrade fails or a database becomes corrupt the model number or system variables may not match, what is the System Variable count for the various controller types?
Environment
All Continuum controllers System Variables.
Cause
For troubleshooting purposes it is often useful to know the number of System variables a controller has. If the numbers differ between on and offline states there is a mismatch or corruption in the database.
Resolution
The following list shows the default number of System Variable objects each model type should contain:
Controller type | # Objects |
bCX1-Inf (9640) | 47 |
bCX1 (4040) | 36 |
bCX1-R (4000) | 36 |
Netcontroller II (9680) | 58 or 61 |
Netcontroller (9900, 9940) | 54 |
CX9400 (Eclipse) | 38 |
CX9200 | 54 |
CMX9924 | 27 |
CX9702 | 41 |
ACX II (5740, 5720) | 63 |
All i2 & b3 Controllers | 35 |
DCX250 | 21 |
ACX700 | 25 |
ACX780, ACX781 | 26 |
i1 Controllers with LCD display support (SCX, LCX810) | 19 |
i1 Controllers without display capability (LCX800, TCX) | 18 |
* Note the Netcontroller II can have 58 or 61 variables depending on firmware version (V2.1x has 61).