Learn about the Community. Join our Core Community to Get Started

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

How does the Automation Server restore script programs state after a power fail condition?

Issue

After a power failure, the Automation Server has a designed procedure to restore script programs in to a particular state. This process should be taken in to consideration when designing the system. 

Product Line

EcoStruxure Building Operation

Environment

Automation Server

Cause

Automation Server loses power and restarts, unsure where script programs will start from once the Automation Server comes back online. Due to the onboard "super cap" saving the database to flash on power loss, are the last script program line and variable values retained for when the Automation Server starts back up?

Resolution

The Automation Server saves it's current active database to flash before losing power completely, the super cap has enough power for it to do this one last task before the Automation Server loses power completely. See AS Power supply interruption or failure on how this is accomplished.

On startup from power fail, any script Programs in the Automation Server will start scanning at the first program line. Make sure to keep this in mind and write your programs so that the first line sets your control values to the default "safe" value before moving on to further control logic.

Tags (2)
Labels (1)
No ratings