How does Modbus scattered read work?

Issue

How does Modbus scattered read work?

Environment

StruxureWare Building Operation 1.5.0 and newer

Modbus

Cause

Optimising communication over Modbus can improve performance.

Resolution

The following is taken from the online help for StruxureWare, Modbus Batch Read Function section. You can view the complete section here:

'Scattered read is an enhancement to the batch read function that enables multiple, non-contiguous slave device registers to be read in a single Modbus query. By using the scattered read function, you can enable the Enterprise Server or Automation Server to avoid reading a large block of contiguous registers when it is only necessary to read a few registers. Also, using scattered read avoids the multiple use of group function codes 03 (analog output holding registers) and 04 (analog input registers) in order to read non-contiguous registers. Group function codes 01 (discrete output logic coils) and 02 (discrete input contacts) are not supported for scattered read.

Scattered read is available only for supported devices, for example, Schneider Electric branch circuit power meters with split core CTs. Furthermore, the scattered read function applies only when the Enterprise Server or Automation Server is operating as the master, not as as a slave. You can enable the scattered read function in the properties of all Modbus devices. However, if a device does not support scattered read, the device is polled by the master device in the same way as if you had not enabled scattered read.'

 

The screenshot below shows the properties dialogue window for a Modbus device