How do TAC Vista server logs affect the performance of the server?

Issue

How do TAC Vista server trend logs affect the performance of the server and LON network?

Environment

TAC Vista server

LON Network

Cause

The bandwidth of the LON network is for all communication on the LON wires to share. This includes all graphics, object transfers, etc.

Resolution

The bottleneck is the communication to the lon network. Depending on what interface (LTA) you are using Vista can handle about 15-40 read/writes per second. Many Vista Server trend logs would increase the amount of information being sent out on the wire and if there is a sufficient number of them, you may see some delays on other forms off communication: i.e., graphics, object transfers, etc.