Function Block program using WDAY with day = Sunday

Issue

When creating a FB program and use WDAY, change the date on the AS or ES to Sunday, the WDAY changes the day to 0 (zero).

Product Line

EcoStruxure Building Operation

Environment

StruxureWare Building Operation and all compatible operating systems including Windows XP, Windows 7, Windows Server 2008, and virtual machine environments.

Cause

Create a FB program and use WDAY, then change the date on the AS or ES to Sunday, the WDAY changes the day to 0 zero.

Steps to reproduce problem:

  1. Create FB Program in AS or ES
  2. Use the WDAY
  3. While using the Graphics Viewer in the AS or ES, WDAY shows correct weekday (today is 2)
  4. Change the date on the AS or ES to a Sunday i.e. 12-09-16 which is Sunday,September 16, 2012
  5. View FB program in Graphics Viewer, which now shows 0 as if today were now 0 

The WDAY FB program should show 7 which is Sunday.

  • Monday=1
  • Tuesday=2
  • Wednesday=3
  • Thursday=4
  • Friday=5
  • Saturday=6
  • Sunday=7

Resolution

This will be resolved in a future release. Currently, there is a alternative: with an XPI block, make WDAY 0 = 7.A second alternative would be to add an if-statement:
if(output = 0){output = 7}
 