Issue

Connecting to an ES that is on another machine through WorkStation and trying to force a BACnet input or output point located on a b3, connected to an AS-P, causes WorkStation to freeze. The only way to get out of freeze is by ending the system task in Windows.

 

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server v2.0.2.x
  • Building Operation Automation Server v2.0.2.x
  • Building Operation Workstation v2.0.2.x
  • Continuum b3xxx Controller any version

Cause

EBO v2.0.2.x has communication issues when connecting to an ES that is not on the machine you have WorkStation on. 

Resolution

Upgrading to 2.0.3.45 or later will resolve this