Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Learn about the Community. Join our Core Community to Get Started
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Forcing BACnet I/O point using ES on another system causes WS to freeze

Issue

Connecting to an ES that is on another machine through WorkStation and trying to force a BACnet input or output point located on a b3, connected to an AS-P, causes WorkStation to freeze. The only way to get out of freeze is by ending the system task in Windows.

 

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server v2.0.2.x
  • Building Operation Automation Server v2.0.2.x
  • Building Operation Workstation v2.0.2.x
  • Continuum b3xxx Controller any version

Cause

EBO v2.0.2.x has communication issues when connecting to an ES that is not on the machine you have WorkStation on. 

Resolution

Upgrading to 2.0.3.45 or later will resolve this

Tags (5)
Labels (1)
100% helpful (1/1)