Issue
Boilers do not operate when HWS output is on.
Environment
Drayton
DC 1100
DC 1400
Boilers not working
HWS
Hot water
Cause
"Boiler Linked" has not been selected in the menu setup.
Resolution
By default the controller does not have the "Boiler Linked" option set.
Set the rotary switch to "Set".
In the display menu structure choose;
- "System Menus"
- "Alter Settings"
- Enter the pass number of 0112 and press enter.
- "Hot Water"
- "Link Option"
- Choose the "Linked Option".
Return the rotary switch back to "Auto"