Failed to call pILiveData error when editing Schedule object in Continuum 1.94

Issue

After upgrading to Continuum 1.94, Cyberstation throws the following error:

Failed to call pILiveData -> GetLiveData().  ACDataServices has an error.

Product Line

Andover Continuum

Environment

  • Continuum 1.94
  • Schedule
  • Error

Cause

This behaviour is due to a bug that was described in TPA-BOST-12-0002 00 Schedule Exception Errors.

Resolution

Install the CyberStation v1.94 SP1 - Software which can be found on the Exchange Extranet.