Learn about the Community. Join our Core Community to Get Started

Schneider Electric Exchange Community

Discuss and solve problems in energy management and automation. Join conversations and share insights on products and solutions. Co-innovate and collaborate with a global network of peers.

Register Now
Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

External resistors required for Biasing and Terminating RS-485 trunks connected to an Automation Server

Issue

External resistors are required for Biasing and Terminating RS-485 trunks connected to an Automation Server (AS)

Product Line

EcoStruxure Building Operation

Environment

  • SmartStruxure Automation Server (AS) with  RS-485 trunk(s) under it.
  • Field controllers on the RS-485 trunk; for example, the Network 8000 ASD controllers (MZ2, PEM1, etc) 

Cause

Bias and terminating resistors are not built into the AS hardware.

Resolution

External resistors are required for Biasing and Terminating RS-485 trunks connected to an  Automation Server (AS).

See the Technical Reference Guide, revision 1.3, pages 2723, 2724, and 2771.

 

Also check out the SmartStruxure-RS485-Network Installation Quick-Help video on the Exchange.

Tags (5)
Labels (1)
No ratings