Error "Invalid Server Type" when attempting to log into the Project Configuration Server (PCS)

Issue

Error "Invalid Server Type" when attempting to log into the Project Configuration Server (PCS)

Product Line

EcoStruxure Building Operation

Environment

StruxureWare Building Operation 1.5 and newer

Cause

Attempting to log into the Enterprise Server IP and Port address with Workstation for Projects

Resolution

Ensure that the Project Configuration Server is installed.

  1. Open Software Administrator and check that the Project Configuration Server tab is shown. If not then the server has not been installed. Install this first
  2. When using Workstation for Projects, make sure you use the correct port setting (HTTP or HTTPS) as defined in the Software Administrator