Error message when you add a new Xenta device to NL220. Lca: Lonmark Self-documentation: Object name too long (Subsystem: NS, #272)

Issue

When you try to insert a new Xenta server into NL220 you receive the error message.

Environment

  • NL220
  • XBuilder

Cause

Controller Object names are limited to 16 character long.

Resolution

In X-Builder, under the SNVT folder, rename the Controller object names to less than 16 characters.