Error flashing Continuum controller firmware.

Issue

An attempt to flash the firmware in the controller results in error:

The UPREV code could not communicate with the specified controller.

 

Environment

bCX

CX9680

ACX5720

ACX5740

Cause

Uprev operation attempted using the wrong flash file.

Resolution

Re-try the operation using the flash file that matches the model number in the controller.

Please note that regardless of what the model number reads from the InfinityController editor in CyberStation the verification is done at the controller level, do not go by what you see in the CyberStation as this user configured field could have been entered incorrectly, verify the model number from the controller's web page configuration.