ERROR C:\Program Files\TAC\TAC Menta X.X.X\temp\opdoc.gop Error in line: xx

Issue

  • If there is a " in any of the Xenta OP screens, the application will not compile/download correctly.
  • Error message states "ERROR c":\program files\tac\tac menta 4.2.3\temp\opdoc.gop Error in line: xx "

Environment

  • Xenta programmable controllers
  • Menta
  • Xenta OP Tree (.dop)

Cause

The character " is not allowed in the Xenta OP.

Resolution

Do not use the character " in the Xenta OP tree.